  1. A command "#1J:100 #2J:100 #3J:100 #4J:100" preceeded by a PVT move is freezing after less than 100 cycles for us (and same for series of CMD). Our supplier reported that he can reproduce it after 29000 cycles. Good news: on our PowerBrick "&1 cpx Inc Rapid A100X100Y100Z100" preceeded by a PVT move is passing 50000 cycles with no problem so far.
  2. In our application we check carefully that the previous move is terminated and this can happen 10 sec after end of previous move. Anyway, without any application involved, the CycleTestPLC mentionned above leads to one motors waiting indefinitetly after a several cycles. I just changed specified this move command: cmd "#1J:-100 #3J:-100 #4J:-100 #5J:-10 #6J:-10". I didn't reproduce the issue with all moves having the same distance. Each cycle duration was pretty stable (+- 5 servo cycles) until it blocked suddenly waiting end of the Jog. From IDE 4.5 terminal I dumped motor 6 statuses after few minutes blocked. For me all the conditions for InPos are met. In the following dump the move is almost finished (but most of the time it is almost not started when it happens): Motor[6].InPos Motor[6].InPos=0 Motor[6].JogPos Motor[6].JogPos=121345495 Motor[6].ActPos Motor[6].ActPos=121345506 Motor[6].DesPos Motor[6].DesPos=121345505 Motor[6].DesVel Motor[6].DesVel=0 Motor[6].ActVel Motor[6].ActVel=0 #6F 2 Motor[6].Status[0] Motor[6].Status[0]=$f100 Motor[6].Status[1] Motor[6].Status[1]=$80000000 Coord[1].Status[0] Coord[1].Status[0]=$1f000 Coord[1].Status[1] Coord[1].Status[1]=$80800001 Motor[6].InPosBand Motor[6].InPosBand=200 Motor[6].InPosTime Motor[6].InPosTime=100 Any suggestion what to do to find the cause, or is there any additionnal information that I should provide ?
  3. It works best with Sys.PreCalc=10 but I had the impression that the freeze occurs more often when the value is small (it might be a false conclusion), which is interesting to reproduce more quickly the problem. I believed that the default value was zero, but It is 1 instead, and if Sys.PreCalc=0 is not good : it make the PVT program fail in RunTimeError often. Anyway I don't see the link between the jogs and the PVT program. I even see some freeze on motors of Coord[2] after we ran the PVT program on other motors in Coord[1]. In your sample program you suggest to get rid of the application and call both the jog and the PVT motion program , right ? Whyis it better in a background PLC than in motion program ? No issue if there are loops of several seconds ? I can see in the dumps that the following error of motors freezed with Inpos=0 is always below 2 cts. Sometimes it happens when ActPos=DesPos=JogPos and most often with ActPos = DesPos != JogPos
  4. Thanks for the comment. Indeed my various tests on the CPU load brings no improvement. The only consistent behaviour is that increasing Sys.PreCalc reduce the frequency of the freezes. In addition to previous described issue, I can find now sometimes a Coord[1] runtime error raised during execution of the PVT motion program that helps to induce the freezes in subsequent "J=XXX" calls. I don't know if this is a clue or completely not correlated. It happens only if Sys.PreCalc=0. The parameters of the program are always the same. As far as I can see the application never request two moves to the same motor in parallel. We do simultneous moves of different motors (either in PVT motion programs or in Jog gpascci commands). I can see in the logs that motors are inPos before accepting a new command that freezes. Most of the time there is at least 10 seconds between the end of the previous move and the subsequent one on the same motor that freezes. I could imagine that if a motor has a bounce (it goes out of InPosBand ) between a check and the command (separated by env 5ms) , it might be bad. I would be surprised that it is the case because it happens randomly with all the motors and they are all tuned carefully. When I have access to the machine next Monday I will measure the cycle thanks to your PLC
  5. Thank you for the suggestions. The issue is that when this happen we see zero in the following error (we have InPosTime=100 meaning 10 ms). The tuning is not the issue since the motor doesn't even start its move. Concerning the runtime error , there is actually no program running, it is a gpasii command that issue the problematic move. Anyway I used to check Coord status from the IDE and there is no error. This is confirmed by the dump above ( Coord[1].Status[0] = 1f000) At the moment I have Sys.MotorsPerRtInt=0, Sys.MaxMotors=17, Sys.MaxCoords=7. I will try to reduce to Sys.MotorsPerRtInt=8, Sys.MaxMotors=15, Sys.MaxCoords=2.
  6. I have a problem on a BrickLV with firmware 2.3.2.5, managing 16 axes, 8 + 8 on a "slave" through macro communication. Our application launches via gpasccii a series very small moves ("J=XXX" commands) , executing in parrallel, and once complete it launches a motion program with PVT moves on 5 motors, and cycling that again and again with the same commands and same moves. Under above conditions I have a probability around 10% to never end the move during processing of the jog commands sent by gpascii. The main symptoms are: one motor among all (the problematic motor number is changing all the time), is blocked with InPos=false but DesVel=0. It often blocks at the begining of the move. Hints: - When I change default Sys.PreCalc to Sys.PreCalc=10 (and keep SegMoveTime=0), I can reduce the failure frequency by a factor of 10 to 50. But none of the parameter values can solve the problem completely. - I can see in Task Manager that regularly I get Bsy/Err in RTI. I tried to change RtIntPeriod and to stop all my PLC, without any improvements. - I tried to group "parallel" jogs in a single gpascii command, but the result is the same. When this freeze happens, I dump the CS and motors status. Here is below one dump result example, where Motor[3] is OK (arrived) and Motor[4] is blocked forever. Motor[3].Status[0] = f900; Motor[3].Status[1] = 80000000; Motor[3].DesPos = -44657.05590625014; Motor[3].ActPos = -44656.50390625; Motor[3].JogPos = -44657.05590625014; Motor[3].DesVel = 0.0; Motor[3].ActVel = -1.0; Motor[3].JogSpeed = 121.2416; Motor[3].InPos = 1; Motor[3].AmpEna = 1; Motor[4].Status[0] = f100; Motor[4].Status[1] = 80000000; Motor[4].DesPos = 5420.312093749992; Motor[4].ActPos = 5420.49609375; Motor[4].JogPos = -860.0027862499992; Motor[4].DesVel = 0.0; Motor[4].ActVel = 0.0; Motor[4].JogSpeed = 6.0398998; Motor[4].InPos = 0; Motor[4].AmpEna = 1; Coord[1].Status[0] = 1f000; Coord[1].Status[1] = 80800001; This non-reliability is critical, so I have been looking for a solution over a long period (before it took hours to get a failure but now I have the script to get it within 1 min). Could you please tell me what might be going on. Is it normal that PreCalc has an such impact on parallel Jog moves ? What kind of solution/configuration could be used to get 100% of the moves finishing ? Thanks, Bernard Lavault
×
×