Leafage Posted August 5 Share Posted August 5 My original axle card (ACC-24E2A [4]) was damaged due to a malfunction, so I purchased a new ACC-24E2A [8]; Currently, I can perform servo on actions and see the current position of the axis, but some information about the axis cannot be correctly fed back to the upper computer. Please seek help! Quote Link to comment Share on other sites More sharing options...
MoMo Posted August 5 Share Posted August 5 Why not apply the same address as before, so there is no need to change the settings in the pmac? Quote Link to comment Share on other sites More sharing options...
Leafage Posted August 5 Author Share Posted August 5 Due to the resumption of procurement for ACC-24E2A [4], it was not purchased Quote Link to comment Share on other sites More sharing options...
Leafage Posted August 5 Author Share Posted August 5 When using ACC24E2A [4] CHAN[0]. Status.a , Will prompt HWChangeErr After executing $$$* * *, the system will recognize the current axis card as [8] by default Quote Link to comment Share on other sites More sharing options...
MoMo Posted August 5 Share Posted August 5 The base address of ACC-24E2A is determined by jumper or Switch, you may need to set it. The system will then recognize it as ACC-24E2A[4]. Of course you need to remove the previously damaged card. 1 Quote Link to comment Share on other sites More sharing options...
Leafage Posted August 5 Author Share Posted August 5 Do you have any information to share with me about the switch settings? Thank you Quote Link to comment Share on other sites More sharing options...
Leafage Posted August 5 Author Share Posted August 5 Is that so? Quote Link to comment Share on other sites More sharing options...
MoMo Posted August 5 Share Posted August 5 I think you should set it like this 1 Quote Link to comment Share on other sites More sharing options...
Leafage Posted August 8 Author Share Posted August 8 It's like this, but I don't understand why the manual in my hand is different from yours. Could you please give me a copy of the manual? Thank you very much.My email address is: leafage2018@outlook.com Best Regards, Otto Quote Link to comment Share on other sites More sharing options...
MoMo Posted August 8 Share Posted August 8 2 hours ago, Leafage said: It's like this, but I don't understand why the manual in my hand is different from yours. Could you please give me a copy of the manual? Thank you very much.My email address is: leafage2018@outlook.com Best Regards, Otto You can download it from the following link: https://automation.omron.com/en/us/support/resources/downloads?filters=type==document&filters=category==manual&filters=tags==delta-tau-legacy&pageSize=10&sort=Recency Quote Link to comment Share on other sites More sharing options...
Leafage Posted August 9 Author Share Posted August 9 Thank you very much, MoMo. I believe all of my issues have been resolved Best Regards, Otto Quote Link to comment Share on other sites More sharing options...