Hi, I have a stepper configured on PowerPMAC BrickLV Firmware 2.5.4.0, using a biss-c 32-bit encoder as position feedback, configured as follow:

 

Encoder:

Acc84B[0].Chan[2].SerialEncCmd = $2114A0

EncTable[13].type = 2
EncTable[13].pEnc = Acc84B[0].Chan[2].SerialEncDataA.a
EncTable[13].pEnc1 = Acc84B[0].Chan[2].SerialEncDataB.a
EncTable[13].index1 = 0
EncTable[13].index2 = 0
EncTable[13].index3 = 0
EncTable[13].index4 = 0
EncTable[13].index5 = 0
EncTable[13].index6 = 0
EncTable[13].ScaleFactor = -1

 

Motor (snippet):

Motor[3].pEnc = EncTable[13].a
Motor[3].pEnc2 = EncTable[3].a

Motor[3].PowerOnMode = 4
Motor[3].AbsPosFormat = $00082008
Motor[3].pAbsPos = Acc84B[0].Chan[2].SerialEncDataA.a
Motor[3].pAbsPos2 = Acc84B[0].Chan[2].SerialEncDataB.a
Motor[3].AbsPosSF = -1

 

I'm facing a problem with power on position settings, due to overflow on Acc84B[0].Chan[2].SerialEncDataA register. There are two experiments of executing #3hmz command on terminal on two different positions of my stage course (see WatchWindow with SerialEncData registers):

 

image.thumb.png.f59f2e6a9f35feb6b76ec44e38e17a71.png

 

 

From position 1 to position 2, I executed a #3j+ command on terminal, and after some seconds, I executed #3j/ and #3hmz commands. The expected behaviour on position 2 is a positive value, not the overflow seen in the test.

 

 

Is there a power on position setting which fix this problem?

 

Link to comment
Share on other sites

  • Replies 3
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

Posted Images

I think your encoder conversion table does not need to use type=2.

Generally speaking, when it is used as an incremental position, you only need to obtain the low-bit data.

The absolute value position only needs to be obtained when the system is started.

Link to comment
Share on other sites

What MoMo says is very true. A type 2 ECT entry to read the second register is not necessary unless it is possible for the source data to change by half the range or more of the “SerialEncDataA” 24-bit register in a single servo cycle. In this case a type = 1 single register read is recommended, as it saves both hardware access time, and software computation time.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.


×
×
  • Create New...