  1. We found a strange reaction of the Brake management in PPMAC.

     

    Use of ouput 2 of Acc11e for Brake:

    Motor[1].pBrakeOut = Sys.piom+$A0000C

    Motor[1].BrakeOutBit = 8 +1;

    Motor[1].BrakeOffDelay = 1000; // en msec.

    Motor[1].BrakeOnDelay = 1000; // en msec.

     

    Brake management OK on these conditions:

    #1out0 or #1J/ --> output ON (brake OFF) + amp enable out ON

    #1dkill or AmpFault --> output OFF (brake ON) + amp enable out OFF

     

    For some reasons, when motor is killed, we want to generate an Amp Fault by, for example, putting "Motor[1].AmpFaultLevel=1"

     

    Status motor gives correct "ampFault =true".

     

    I this case, if we do #1out0 -->

    Amp Enable output stays OFF (normal as Amp Fault), but the output goes ON (brake OFF).

     

    Is this normal?

×
×