Hi,
Is it possible to configure a global variable from communication-thread D-variables?
I cannot access the position readback of virtual axes individually from a PLC file, and I don't know why. I just want to map a readback position to a Q variable, but it is not that easy from a PLC file...
The only thing I want is the numerical response for one axis, not string for all axes like the output for "&1p" command.
Example:
&1p
X111 Y222 // string output with all axes set in D0 mask
&2p
X333 Y444
I can access the desired values with commands like:
&1D // Apply "CS1 environment" to D-variables
X111 Y222
D6 // Query CS1 axis X position
111 // this is the output I want
D7 // Query CS1 axis Y position
222 // this is the output I want
&2D;D7 // Change D-variables to CS2 environment; query for CS2 Y position
X333 Y444 // first command output (undesired)
444 //second command output (desired)
But these commands only work from communications threads / scripts other than PLC files.
So I tried to access from PLC file the D-variables from coordinate systems and PLCs, but these are different domains.
What I am missing? How can I access these values from PLC?
Controller: Power Brick LV
Best regards,
Marcelo Moraes
-
If you can reduce the external inductance to a value of 1mH, you can achieve the highest capability of Geo Brick LV.
Hi Sina,
I am facing the same problem with PWM amplifier + low-inductance motor.
Motor:
Inductance line-line = 1.7 mH
Resistance (25 deg Celsius) line-line = 4.4 ohms
tau_sec = 1.7e-3 / 4.4 = 386.36 usec => minimum_PWM_f ~ 8 kHz
The PWM frequency is set to 20 kHz (maximum recomended value for my amplifier), and the open-loop noise (#1out0) is too big.
We tried to supress the noise by adding 1 mH inductance in series, which attenuated it but didn't achieved our stability spec. Then we tried bigger inductance values, but it didn't work very well.
How did you calculate the optimum value of series inductance?
What would be the optimal value for my scenario?
Controller: Power Brick LV (5 A / 15 A amplifier)
Regards,
Marcelo Moraes
Coordinate systems D-variables
in Power PMAC
Posted
Thank you very much, curtwilson.
PREAD is the exact command I was searching for.