Posted (edited)

When i have a fault on a 1S drive I want to read the specifics of the fault from my PMAC.  I've toyed with retrieving the Sysmac Error Status (0x2002:01) and similar but it has caused errors and EtherCAT will not activate.  Are there any suggestions for doing this?  Hopefully there is just an Application Note I've missed.

 

Thanks in advance,

Edited by MarkDR
Link to comment
Share on other sites

  • Replies 5
  • Created
  • Last Reply

Top Posters In This Topic

Popular Days

Top Posters In This Topic

The “1S” error codes are found in object “Index 4000h”. There are three subindexes. See section “9-8-1” of the “1S” manual for details.

You can read these in PMAC using the “ecattypedsdo()” function. This is documented in the “Power PMAC Software Reference Manual” in the chapter “Power PMAC Script Mathematical Feature Specification” specifically in the section “EtherCAT Network Functions” on page 1566.

Here’s an example of reading “subindex 81 hex (Error Full Code)”.
Function arguments:
EtherCAT network index = 0 (your value needed)
EtherCAT slave index = 0 (your value needed)
Direction of access = 1 (read)
Index number of SDO = $4000
Subindex number of SDO = $81
Dummy data value = 0
Data size = 4

Usage in a program or as an “on-line” command (trailing “L0” reports the result):
L0 = ecattypedsdo(0,0,1,$4000,$81,0,4)
L0 = ecattypedsdo(0,0,1,$4000,$81,0,4) L0
 

Link to comment
Share on other sites

The “ecattypedsdo()” function should not be used cyclically as it interferes with the mapped PDO network synchronization. This should only be used infrequently in an “on-demand” need. For “cyclic” needs this should be mapped as a PDO.

This is may have already been mapped through the “Mirror” object, 603F hex (Main code only, 4000 hex: Error Full Code, Subindex 82 hex: Error Code), if you have selected the “258th transmit PDO Mapping” in the “PDO Mapping” tab of the “Device Editor” for that 1S drive.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.


×
×
  • Create New...