Richard Naddaf Posted August 10, 2011 Share Posted August 10, 2011 If the Macro ring is not up, any Macro communication commands can cause the USB/Ethernet processor to not detect the PMAC cpu. Furthermore, the ModBus (if configured) configuration will not be retrieved. In general, regardless of ModBus status, do NOT send any Macro communication commands until the Macro ring is active, and faults are cleared. Clearing Macro Station (at least 1st MACRO IC), and Ring Controller Macro faults in a start-up PLC (see example below) should alleviate this problem. Note that this requires I80, I81, I82, MS{},I8, MS{},I9, and MS{},I10 to be set properly. The Ring Active bit is in the Global Status word. End Gat Del Gat Close #define RingActiveBit M8000 #define ClrfRequest P8000 RingActiveBit->Y:$6,9,1 ; Macro ring active bit - Must have I80, I81, I82 set ClrfRequest=0 ; Macro clear faults request flag Open PLC 1 Clear ClrfRequest=1 ; Request to clear Macro Faults If (RingActiveBit=1 AND ClrfRequest=1) CMD"MSCLRF15" ; Clear Faults Macro IC0 I5111=250*8388608/I10 while(I5111>0) endw ; 250 msec delay CMD"CLRF" ; Clear Faults Macro IC0 I5111=250*8388608/I10 while(I5111>0) endw ; 250 msec delay CMD"MSCLRF15" ; Clear Faults Macro IC0 I5111=250*8388608/I10 while(I5111>0) endw ; 250 msec delay ClrfRequest=0 ; Reset request flag EndIF Close Link to comment Share on other sites More sharing options...