RS232 connected, to load the backup file.

Load the parameters.

Load movement programs.

I can not load the plc.

ER003 executing "open plc 0 clear"

  • Replies 3
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

Posted

if there is a structural or syntax problem in any of your PLC's this will happen. Could one of the PLC's have a bug, i.e. missing some code?

 

Using the terminal. I can run "open prog 1 clear". but I can not "open plc 1 clear". ER003

This PMAC Was off for 4 years.

I change the battery

Posted
The "open plc 1 clear" command sequence should not cause an "ER003" by itself. If the batterry was dead the PMAC may have corrupted memory. After changing the battery issue a "$$$***" and then reload your configuration.