piefum Posted January 9, 2013 Share Posted January 9, 2013 Hi All I am having problem with one Geo Macro GM15-2 that we bought a couple of years ago. I am using one of the GeoMacro that was intended to be a spare: this GM has been successfully used only for few hours in June 2011, than has been put aside. I resuscitated this driver in order to test the spare actuator unit, and now I have some issue regarding the PLIM and MLIM input of GM channel #1. It seems that the MLIM1 is insensible to any signal connected to it: the same signal that engage or disengage the PLIM1, MLIM2 and PLIM2, is not doing anything on MLIM1. Do you have any idea on how to operate or better understand what is happening on this connector? thanks gigi Link to comment Share on other sites More sharing options...
steve.milici Posted January 9, 2013 Share Posted January 9, 2013 Try a non solid state device (real switch) to test. This could indicate a borderline conductivity or current draw issue on this channel. Link to comment Share on other sites More sharing options...
piefum Posted January 10, 2013 Author Share Posted January 10, 2013 Try a non solid state device (real switch) to test. This could indicate a borderline conductivity or current draw issue on this channel. I just tried shorting all the input ports to VCC or GND: it works on PLIM1, MLIM2 and PLIM2, but not on the MLIM1. Link to comment Share on other sites More sharing options...
steve.milici Posted January 10, 2013 Share Posted January 10, 2013 If you are certain the unit is properly configured to see the limit then this would indicate that something has compromised the input - this will probably require repair. Link to comment Share on other sites More sharing options...