I have two motors setup the same way, but the reading of the encoders differ by a factor of 32 when they are in the same position.

 

I'm using a Absolute position Renisaw Biss C encoder. The resolution is 0.05 um, so I use a Ixx08=20.

 

For motor 1 I get the following readings: (This is correct)

The encoder sends 500000 in 26 bits. I process this data with the conversion table using Parallel Y word data, No filtering, and Normal Shifted, and so I get: (I8000=$278c00 I8001=$01800)

X:$3501 is 500000

X:$3502 is 0

I join this two in the recommended variable for actual position:

M162=(X:$3501 + X:$3502)*I108 (Not the actual code line)

=500000*20=10000000

And the Position Window in Pewin 32 reads 500000 cts.

 

This is correct. However, motor 3 is configured the same way, and makes all the calculations in the right way. But, the position Window in Pewin 32 reads 15625 cts. Is wrong by a factor of 32.

 

Im using a total of 4 motors, and only motor 3 makes this extra calculation.

 

Were does the Position Window of Pewin 32 takes the values from? Which variable.

 

Any ideas on what can be wrong?

 

 

THANKS

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

Did you try swapping encoders with channels to see what happens?

Can you share your full setup parameters?

What hardware are you using (e.g. ACC-84E, Brick)?

Did you check to see if the position window in the PeWin is not scaled differently for channel 3?

What do #2P#3P report at those locations?

What do the serial encoder registers A and B read at those locations? You should use these to compute actual position.