Jump to content
OMRON Forums

Recommended Posts

Posted
I want to interface SSI multiturn encoder to ACC-53E/ACC-84S. Multiturn resolution will be 12 bits and single turn resolution will be 17 bits. The encoder output will be in extended SSI format as specified in attachment. Is this possible ? As per my knowledge, currently encoder conversion table does not have a format to allow this.

Technical_Manual_SSI_BiSS_ACURO_en.pdf

  • Replies 4
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

Posted Images

Posted

Abhijit,

 

Based on the description and diagram of the Extended SSI Protocol on page 8/29 of the document you attached, the single-turn data is first transmitted, followed by the multi-turn data, and the position data seems to all be contiguous. The position data appears to all be transmitted before any of the status bits are transmitted. If this is all true (you should double-check it), then ACC-84S can handle the position information. In the Channel-Specific Control Word involved in setting up the ACC-84S in software, you need to specify the exact number of bits of position information to use in order that the PMAC will not mistake any of the status bits for position bits.

 

Below is an image demonstrating an example of how the position information needs to be arranged within the serial encoder data registers on ACC-84S:

 

serial_data_registers.png.78cba54ddb8f3c34f30331b1a2e8adf8.png

  • 2 weeks later...
Posted

Thank you for the information.

 

Does this apply to brick controller, geo brick drive and geo pmac having appropriate options selections for absolute SSI encoder feedback ?

Guest
This topic is now closed to further replies.

×
×
  • Create New...