Mattlyf Posted January 30, 2015 Share Posted January 30, 2015 I have a Geo Brick LV-PC, I'm trying to setup some PI servo motors. The motors drive fine in open loop mode with #xo30, #xo-30 etc but when I drive them with a jog command #xj+, #xj- etc it goes out on following error. When I set it to ignore the error I noticed the counts are going the wrong way, so if I give #xj+ the counts go negative, if I give #1j- the counts go positive. The motor is going in the correct direction when driven. I've tried swapping encoder wiring A with not A and B with not B but that made no difference, so I then tried A with B and not A with not B, this resulted in the motor not driving at all in closed loop. Has anyone else experienced this or have any pointers as to where to start looking? Thanks Link to comment Share on other sites More sharing options...
Highland Controls Posted January 30, 2015 Share Posted January 30, 2015 You should have swapped either A+ and A- or B+ and B-. The other option is to change I68n0/I69n0 to the opposite direction. Probably at 3 now, should change to 7. Link to comment Share on other sites More sharing options...
Mattlyf Posted January 30, 2015 Author Share Posted January 30, 2015 Hi, thanks for the reply, changing the variables worked. Thanks Link to comment Share on other sites More sharing options...