Gaggstatter Posted July 16, 2015 Share Posted July 16, 2015 We currently have this limit (I211) set to: 7,060,411. We need to have it 5 times higher for some specific types of movement, but this variable only allows: 8,388,607 units. What is the simplest way to scale this limit? Link to comment Share on other sites More sharing options...
steve.milici Posted July 16, 2015 Share Posted July 16, 2015 There is no way to scale this other than re-scaling your feedback (and then of course your gains/Ixx08-Ixx09 values appropriately). Why do you need such large values of FE? Link to comment Share on other sites More sharing options...
Gaggstatter Posted July 20, 2015 Author Share Posted July 20, 2015 Thanks for your answer Steve. This are not very high values in our system configuration, although they are higher than the usual ones. It's just when the telescope slews (1.0 deg/s) to the target we don't mind about the following error, as long as it's kept inside a safety range. The current following error is low enough to stabilise the telescope when being on tracking and doing acquisitions, in this case the telescope moves at a much slower rate (often around 0.01 deg/s). So we want to have a kind of dynamic fatal following error limit, depending on type/speed of the current movement. Could you please explain the procedure to re-scale the feedback? I see that Ixx08=1 and Ixx09=1 on our current application. Link to comment Share on other sites More sharing options...
steve.milici Posted July 20, 2015 Share Posted July 20, 2015 We need to find a way to physically reduce the count density of the feedback device. Typically once there is a reduction, Ixx08 and Ixx09 would be increased by the same ratio (assuming the same sensor for both Ixx03 and Ixx04) to allow the same PID values, or, maybe some intermediate adjustment of 1xx03/04 and gains. You would then maintain two different sets of ECT entries, one set for the regular feedback and one set for the reduced feedback. To switch between the two feedback device (even on the fly) is simply changing Ix03, Ix04, previous actual position, and previous actual “velocity” position in a single servo cycle in a PLC0. I know you have a number of special filters and user servo – I’m not sure how this will impact the situation so I will need some details on your feedback setup and these connections. Example from motor #1 to Motor #2 (UMAC): (From the SRM memory map section) Y:$000x8A/0A Motor previous actual source position value Y:$000x9D/1D Motor previous velocity-loop source position M1->Y:$8A,0,24,S ; Motor #1 Previous Actual Position M2->Y$9D,0,24,S ; Motor #1 Previous ‘Velocity’ Position M3->X:$3502,0,24,S ; Encoder #2 ECT converted data OPEN PLCC0 CLEAR I103 = $3502 ; Was $3501 (default) I104 = $3502 ; Was $3501 (default) M1 = M3 M2 = M3 DISPLCC0 CLOSE Link to comment Share on other sites More sharing options...
Gaggstatter Posted July 22, 2015 Author Share Posted July 22, 2015 From what I understand from your explanation, the way to reduce the count density would be inside the ECT, could you be more specific how could I achieve this? And which other parameters would be affected due to this scaling? I think it's not needed to re-scale the feedback on the fly, once this new reduced ECT configuration is established I can change the fatal following error limit forever, this seems easier and less error prone to me, or am I wrong? Do you need any variables information or configuration? Please let me know and I can post it here or send it to you by email. Link to comment Share on other sites More sharing options...
steve.milici Posted July 23, 2015 Share Posted July 23, 2015 Basically we could process the raw encoder register in the ECT as a parallel x word and not shift to get 32 times reduction but as I remember your feedback was not out of a gate encoder register but some memory location generated by a PLC0 or user servo. I will need to know the details of how your feedback is done to come up with a workable scheme. Link to comment Share on other sites More sharing options...
Gaggstatter Posted October 5, 2015 Author Share Posted October 5, 2015 Sorry for the interruption, we were working on other higher priority projects. Giving some time to this again. Two questions have arisen: 1. When I reduce the gear ratio from the feedback, lets say I would divide it by 32, isn't there a loss of resolution? 2. Would an alternative where I just disable the internal limit and use a variable for checking in our user written servo be a valid approach? Or could this somehow be dangerous? I mean this is the only known part of the code where a new demand to our servo drives is calculated, this is why I came up with this place being the apparently optimal, as here is where the following error is used to produce a new demand. Link to comment Share on other sites More sharing options...
steve.milici Posted October 6, 2015 Share Posted October 6, 2015 There would not be a loss of resolution as the LSB of the feedback device would still be used if this is currently an ECT processed encoder from a PMAC servo gate. What is the source of this feedback? Your approach in #2 is valid (could also be in a background or RTI PLC) but you may want to have a "check", as in a simple counter, that any program move could check first that the code is running whether it is a user servo or a PLC (background or RTI). Even user servo could be inadvertently deactivated with Ixx59. Link to comment Share on other sites More sharing options...
Gaggstatter Posted October 8, 2015 Author Share Posted October 8, 2015 Thanks for your answers Steve, but the one about #2 I'm not sure to have understood it. What did you mean about having a "check"? If user servo is disabled this would be dangerous so do you mean apart from the UserServo modification, another PLC that checks that Ixx59 is active and if not doesn't allows to move? I wanted to implement something like this in the user written servo code section: Tracking is the slow high precision movement, and slewing the faster one. If (MTRNUM = 2) ;Checks if a slewing period starts If (isTracking = 1) And(current_velocity > min_slew_velocity) isTracking = 0 I211 = 0 EndIf ;Checks if a tracking period starts If(isTracking=0) And(current_velocity < min_slew_velocity) isTracking = 1 I211 = tracking_fatal_following_error_limit EndIf ;Stops the movement if higher following error exceeded If (following_error > slewing_fatal_following_error_limit) COMMAND"#2k” RETURN(0) ;Break execution and return zero current demand EndIf ;Here new current demand depending on current and demanded position is calculated with PID ... RETURN(DAC) EndIf Here is our current ECT setup, we are only using motor #2 as a real motor, feedback is obtained from encoder on motor#1, and motor #3 is for synchronization purposes, if you need any more info please don't hesitate to ask us for it: I8000=$F60460 I8001=$218000 I8002=$78000 I8003=$78008 I8004=$78010 I8005=$78018 I8006=$E00203 I8007=$E00405 I8008=$E00607 I8009=$2810FE I8010=$18000 I8011=$E20A08 I8012=$EC000B I8013=$D03509 I8014=$7FFF I8015=$A I8016=$2F8430 I8017=$18000 I8018=$2F8434 I8019=$18000 I8020=$2F8438 I8021=$18000 I8022=$2F843C I8023=$18000 Link to comment Share on other sites More sharing options...
steve.milici Posted October 8, 2015 Share Posted October 8, 2015 By “check” I mean something that positively determines the user servo (or PLC) is running. A counter would be a very simple technique, as in P99=P99+1. The host computer, or other PMAC program starting motion or closing the loop, would check that the counter is in fact counting. If motor #2 is looking at a real encoder you could have another ECT entry to implement my #6 post. Link to comment Share on other sites More sharing options...