Jump to content
OMRON Forums

Power clipper, J4 connector flag inputs status


LECA1239

Recommended Posts

In power PMAC clipper, J4 connector flag inputs status, initially shows 1(high) .And when flag input is connected to 0 volt supply, flag status shows to 0(low). We need to change the polarity of flag status. We want to configure Flag Inputs as general purpose digital inputs. Can you recommend solution for this issues .

 

Example:

In J8 and J9 connector we have one bite for changing the polarity of the inputs : Clipper[0].GpioPol[0] = $0000FFFF // Polarity Control (INPUTS IS SHOWS 0 OR 1 SETTING ).

 

Question:

Is there any bit setting or any other method to change the polarity on J4 .

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

You can only invert the "software" polarity" of the port with Clipper[0].GpioPol[0]. To change the inversion from the default (see the manual for details) for just the inputs of the JOPT port set Clipper[0].GpioPol[0] = $00FF0000. Note that Clipper[0].GpioPol[0] is the inversion control for both the JOPT and JTHW prot. The high 16 bits is for the JOPT - the inputs are the 8 MSBs of this.

 

The actual hardware is fixed with a 10KOhm pull-up resistor to +5v.

Link to comment
Share on other sites

Guest
This topic is now closed to further replies.

×
×
  • Create New...