wlewis

Recommended Posts

  • Replies 3
  • Created
  • Last Reply

Top Posters In This Topic

Yes, you can.

 

These are the ring controller settings:

 

// First MACRO Gate

Gate2[0].MacroMode = $4030

Gate2[0].MacroEnable = $0FF333 // 8 SERVO NODES ENABLED, ENABLE I/O NODES AS NEEDED

 

// If you have a second Gate

Gate2[1].MacroMode = $10

Gate2[1].MacroEnable = $180000 // ENABLE NODES AS NEEDED

 

// If you have a third Gate

Gate2[2].MacroMode = $10

Gate2[2].MacroEnable = $280000 // ENABLE NODES AS NEEDED

 

// If you have a fourth Gate

Gate2[3].MacroMode = $10

Gate2[3].MacroEnable = $380000 // ENABLE NODES AS NEEDED

 

// Ring check settings

Macro.TestPeriod = 20

Macro.TestMaxErrors = Macro.TestPeriod / 2

Macro.TestReqdSynchs = Macro.TestPeriod - Macro.TestMaxErrors

 

The slave (Brick) settings are exactly the same as in the Brick manual for MACRO auxiliary mode communication (using Ixx44).