guoke1225 Posted January 31, 2019 Share Posted January 31, 2019 I build up Modbus TCPIP communication with UMAC successfully, for the coil and discrete read/write , it is worked normally. and for the registers read/write, it seems that only 16-bit registers can worked normally. because of bit 16 to 23 for X:memory and Y:memory are not used, if I define a register which bits is larger than 23 bits, the data received is wrong. and if I define a register which is a float type value, It can't receive data. M2040->L:$107A4 //pointer to 48 bits value. M2041->F:$107A5 //pointer to float type value. so is there any solutions to avoid this issue? read/write values which bits is larger than 23 bits, and read/write float values correctly. Link to comment Share on other sites More sharing options...
Omron Forums Support Posted April 10, 2019 Share Posted April 10, 2019 Hopefully this is better late than never. Using 2 UMACs, one as client and one as server, I am able to receive float data that is sent in IEEE 32 bit float format. For instance, 00111111100000010100011110101110 is roughly 1.01. I broke that into two Modbus registers and converted into decimal: 0011111110000001 = 16527 0100011110101110 = 18350 M1->X:$10780,16 M2->Y:$10780,16 M1 = 16527 M2 = 18350 I set up Modbus with FC16, Modbus Ref#0, PMAC Ref#0, Count length 2. Then, on the Server: M1->F:$10780 M1=1.0099999905 PMAC reads in using big endian format, so maybe you need to either convert to big endian or rearrange the byte assignments in PMAC. Link to comment Share on other sites More sharing options...