Omron Forums Support Posted March 14, 2022 Share Posted March 14, 2022 You will have to convert the HT of the scanner to a keyboard tab. Program the scanner postamble to HT, then do a momentary key binding on the IB-3PC of HT to tab Setup IB-3PC: Connect the IB-3PC to the keyboard port of the PC and the keyboard to the IB-3PC. - Connect the serial cable to the IB-3PC and your com port. Set the switch to 2. - Start hyperterminal and connect at 9600,E,7,1, no flow control - Send to mute the IB-3PC. - Send to verify the connection. You should recieve an answer form the com port. - Send to configure, disable muting and save. Help: Help on programming of the IB-3PC can be found from page 2-4 of the manual. Quote Link to comment Share on other sites More sharing options...