Omron Forums Support Posted March 14, 2022 Posted March 14, 2022 Depending on the press and camera mounting positioning, there is a possibility of vibration transferring from the press into the camera mount. Check the camera lens to insure it is secure.Check all mounting hardware to insure the camera mount has not shaken loose over time. The mount may feel secure, but a bolt being slightly loose is all it take to cause movement.It is best to check all connections with a wrench.If all connections are solid, try running the press at a slower or faster speed to minimize the amount of shake in the machine. The press may have a certain speed that causes resonance, and by changing the speed of the press, this can be eliminated. ` Operating System Any Quote