QX Hawk Daisy Chain Setup

Setup Secondary QX Hawk cameras first
Read Cycle > Trigger = Serial Data
Read Cycle > End of Read Cycle > Mode = Timeout
Read Cycle > End of Read Cycle > Read Cycle Timeout = 20ms less than previous camera in daisy chain
Symbologies  > Data Matrix > ECC 200 = Disabled
Symbologies  > Code 39 = Disabled
Symbologies  > UPC/EAN = Enabled
Calibrate camera (or set Gain, Shutter, & Focus values)
Send and Save to camera (<Z>)
Confirm proper reading via serial trigger (<space>)
               < >
Repeat for each secondary camera in daisy chain
Setup Primary QX Hawk Camera
(if desired) Comm > Array Comm > Daisy Chain ID Status = Enabled (Shows which camera read the code)
Read Cycle > Trigger = Serial Data
Read Cycle > End of Read Cycle > Mode = Timeout
Read Cycle > End of Read Cycle > Read Cycle Timeout = max time per application
Symbologies  > Data Matrix > ECC 200 = Disabled
Symbologies  > Code 39 = Disabled
Symbologies  > UPC/EAN = Enabled
I/O – Set desired Output configuration (Symbol Data Output, Output 1,2,3 parameters)
Matchcode > Matchcode Type = Enabled
(if desired) Matchcode > Mismatch Replace = Enabled
Utilities > Master Database > enter desired match string
Calibrate camera (or set Gain, Shutter, & Focus values)
Send and Save to camera (<Z>)
Confirm proper reading via serial trigger (<space>)
               < >
In Terminal enter the following command
               <K150DAISY>
You should see a response like:
<DAISYCHAIN: Slaves = 1><DAISYCHAIN: Units Resetting><DAISYCHAIN: setup complete><DAISYCHAIN: resetting master unit>
Cycle power to the cameras.  Otherwise the camera may not respond to triggers properly.
Connect to the Primary unit again and change Read Cycle > Trigger = External Edge
Send and Save to camera (<Z>)
When the <K150DAISY> is executed, the trigger mode on the secondary camera change to match the primary.  By executing the <K150DAISY> when the trigger = Serial Data, the secondary units will only respond to a serial trigger to start the read cycle. 
If the primary camera has the trigger = External Edge, then after the <K150DAISY> all of the secondary cameras will be responding to the external trigger as well.  This did appear to work in the limited testing in the office.
MD – 2017-02-07

Operating System

Any

Link to comment
Share on other sites

  • Replies 0
  • Created
  • Last Reply

Top Posters In This Topic

Popular Days

Top Posters In This Topic

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.


×
×
  • Create New...