Omron Forums Support Posted March 14, 2022 Share Posted March 14, 2022 The Vision HAWK and Vision MINI will refuse to boot with many of the LED indicator lights remaining on if the following conditions are met: 1) The serial port is set to VxWorks (via the "BP_UpdateConsoleTTY 2" command and 2) The serial port is floating (not connected to anything). The workarounds currently are to either connect the serial port (grounding the Rx and Tx are sufficient or to set the serial port connection to none or VsApp ("BP_UpdateConsoleTTY 0" or "BP_UpdateConsoleTTY 1"). Quote Link to comment Share on other sites More sharing options...