CK3E EtherCAT Acontis - howto accomplish bus shift mode
sutty replied to sutty's topic in Power PMAC
Thanks Steve! I upgraded using IDE V4.3.2.19 from V2.5.0.3 to V2.5.4.0 - and lost gpascii and other stuff - no connection to ppmac anymore. Serially I can still conect. /opt/ppmac only shows usrflash and usrflash.x directories, nothing else anymore. So how to successfully upgrade from V2.5.0.3 to V2.5.4.0 resp reinstall the lost directories?! -
Hi! I run CK3E (2.5.0.3) with 2 Omron 1S-drives (Rev 10001). In master shift mode it's fine. Howto accomplish bus shift mode?! Why still do I have to set "ECAT[0].DCRefMaster=1" after loading Mapping to PowerPMAC?! What I do (without success) 1. set Clock adjustment to bus shift 2. Click "Load Mapping to PowerPMAC" 3. Set using terminal "ECAT[0].DCRefMaster=1" (where point 2 let it at 0) 4. Clicke "Activate EtherCAT" Why wihtout success: The drives would run in CSP, but reading the slaves register 0x92C would give for the first slave steadily 0 (!) and for the second slave <>0. Both should deliver <>0 values in case of bus shift mode. Regards, Anton
-
IDE V4.3.2.19 Motor Commission Motor Acceleration Controll buggy
sutty replied to sutty's topic in Power PMAC
Thank you Atul! Maybe it was not clear - here a screenshot. First I entered into the terminal Motor[1].InvAmax=1 and let Motor[1].InvDmax=0.1 The UI shows wrong values with 1E-06 and 1E-07 for InvAmax and InvDmax. -
Yes, I did chose ethercat for the topology! Concrning the ESI - does anybody confirm those importing error, or is it only my deal?!
-
Hi! Entering values to Motor[x].InvAmax rsp Motor[x].InvDmax get wrongly displayed in IDE Solution Explorer - Motor – Commission – Motor Acceleration Control – Max. Programmed Accel. rsp Max. Programmed Final Decel for values < 10 The other way around works correctly. See attached file. 200319_ODT_IDE_V4.3.2.19_bug_i117.pdf
-
I did inform Beckhoff on March, 12th - no reply so far. Remark: Inporting the ESI-Zip into TwinCAT3 does not produce any error. Still, I will insist once more... Actually importing the whole ESI-Zip from Beckhoff (02/21/2020) produces a bunch of errors. Could this still be an issue of EC-Engineer/IDE, or not?! --------------------------- EC-Engineer --------------------------- ESI file 'Beckhoff AX8yxx.xml' is invalid and can not be added: The element 'Profile' has invalid child element 'ScalingTable'. List of possible elements expected: 'VendorSpecific'. (Line: 5205, Position: 7) --------------------------- ESI file 'Beckhoff EJ7xxx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 102116, Position: 72) --------------------------- ESI file 'Beckhoff EL5xxx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 158703, Position: 51) --------------------------- ESI file 'Beckhoff EL72xx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 127196, Position: 72) --------------------------- ESI file 'Beckhoff EL73xx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 142194, Position: 72) --------------------------- ESI file 'Beckhoff EL7xxx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 359738, Position: 72) --------------------------- ESI file 'Beckhoff ELM31xx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 283221, Position: 72) --------------------------- ESI file 'Beckhoff EP3xxx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 221684, Position: 42) --------------------------- ESI file 'Beckhoff EP7xxx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 327728, Position: 72) --------------------------- ESI file 'Beckhoff EPP3xxx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 87790, Position: 42) --------------------------- ESI file 'Beckhoff EPP7xxx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 26247, Position: 72) --------------------------- ESI file 'Beckhoff EtherCAT Terminals.xml' is invalid and can not be added: The 'Physics' attribute is invalid - The value 'BB' is invalid according to its datatype 'PhysicsType' - The Pattern constraint failed. (Line: 173, Position: 12) ---------------------------
-
After removing all 'SdoUploadWithMaxLength' I succeded importing the ESI-File into IDE V4.3.2.19. Can I use this manipulated ESI-File without concern? But including the EL7211-0010, which actually is a drive, as a drive in the motors topology view does not work. There it does not show up at all. Will I have to do it by hand (commissioning - advanced settings), or is there some easier way?!!
-
Hi! On IDE V4.3.2.19 and also V4.2.0.19 I am trying to import ESI XML-File "Beckhoff EL72xx.xml". But it fails with EC-engineer error message: ESI file 'Beckhoff EL72xx.xml' is invalid and can not be added: The 'SdoUploadWithMaxLength' attribute is not declared. (Line: 127196, Position: 72) The XML-file I've downloaded today from: https://download.beckhoff.com/download/configuration-files/io/ethercat/xml-device-description/Beckhoff_EtherCAT_XML.zip Importing an older XML-file from July 2017 does not fail. I also send an inquiry to Beckhoff. Regards, Anton
-
Hi! Using a PMAC2-style Servo IC (DSPGate1 Rev D, like in Acc24E2) by when will OneOverTEna (Hardware 1/T) be available on Power PMAC?! Best Regards, Anton
-
RESOLVED - Motor[4].Desired.Pos delivers nan (not a number)
sutty replied to sutty's topic in Power PMAC
This was my mistake - excuse me, Curt! After initialization-sequence in plc1 Motor[4].AbortTa would hold "-inf", what leads to "Motor[4].Desired.Pos=nan", and finally what blocks the start of any motion prog. -
Hi! I have 8 active motors, where always 2 are cascaded (#1 with #21, #2 with #22, #3 with #23, #4 with #24) I use plc2 to start motion prog 10 in Coordinate-system &1: open plc2 plc[2].ldata.coord=1 jog/21..23 jog/24 enable 1 sys.cdtimer[3]=500 while (( sys.cdtimer[3]>0) && (m281==0 || m282==0 || m283==0 || m284==0)) // wait for desvel=0 { // } if ( sys.cdtimer[3]!>0) { M611=62 // Timout enable servos CS1 } else { abort 1 start1:10 // Joystick Prog start } disable plc2 close Using 3 (6) active motors (XYZ): - plc2 starts prog10, and it works correctly Using 4 (8) active motors (WXYZ) - plc2 starts prog10 but prog10 does not run (listpc shows line 1 of prog10) and delivers Motor[4].Desired.Pos=nan, - typing all the commands of plc2 manually into a terminal starts prog10 correctly - Issuing #24j/#4j=0 before launching plc2 let run prog10 correctly - after all, once Motor[4].Desired.Pos has a real number, prog10 can be started from plc2 any time without any problem What is going wrong here?! Regards, Anton
-
Hi! We are running a PPMAC ARM V2.3.2.5 on Phase/Servo/RTI 32/16/2 kHz, 2x3 cascaded motors (6 motors) Running the application w/o Lookahead doesn't cause any problems. But with Lookahead active (10ms Segmentation, 130 Segments) once in a while (every several minutes up to every several hours) run-time error occurs. Unfortunately, Coord[x].Ldata.Status always tells a 1 after such run-time error - it does not give any useful information. What is very confusing to us is that a few milliseconds before run-time error occurs Sys.RtIntTime peaks for the duration of only 1/16 of a millisecond!! Another characteristic is that as long Sys.RtIntTime stays below 750 us run-time error does not show up at all. Augmenting Sys.PreCalc does not help. Removing RtiCplc does not help neither. At last whenever a run-time error happens it almost always shows this kind of pattern. Today we started testings with V2.4.1.2 - results will follow. Questions: 1. Why would Sys.RtIntTime peak for less than 70us?! 2. Any suggestions which PPMAC-Variables to trace to get more useful data? Best Regards, Anton
-
Hi Stephen! On Turbo PMAC there was a real run-time error status-word with a bunch of bits telling the cause of any run-time error: = 1: Insufficient calculation time = 2: Program counter out of range (too low) = 3: Program counter out of range (too high) = 4: Unlinked conditional statement = 5: Subroutine stack overflow = 6: Jump to non-existent label = 7: Cutter compensation interference error = 8: Forward kinematic execution error = 9: Inverse kinematic execution error = 10: No axes remaining in C.S. On PPMAC there is only that one and only bit 16 in Coord[x].ErrorStatus - nothing else more anymore. Or am I missing up something?! Regards, Anton
-
Hi there! I am running a UMAC ARM PPMAC with Acc24E3. It seems to be an issue related to the overall load of the PPMAC, which is about 50% on both cores. I've tested two variants: With V2.4.1.2 and IDE 4.1.0.24 With V2.3.2.5 and IDE 3.0.1.0 On both Sys.ServoErrorCtr, Sys.ServoBusyCtr are incrementing on closing any window like Plot, Tune, Task-Manager...even on closing the IDE itself. After a $$$***, so almost no load, this behavior does not show up. Regards, Anton
-
Hi! In case of run-time error Turbo PMAC provided run-time error codes (Y:$002x14) ! Does Power PMAC also provide such informations?! Thanks, Anton
-
Hi! I was wondering why Sys.ServoErrorCtr would get bigger than 0 at all. Then I realized, whenever I close one of the windows within IDE (Plot, Tune, Task-Manager,...) or even open or close the IDE itself, Sys.ServoErrorCtr would increase tremendously. Can anybody copy this behavior?! Regards, Anton
-
By when will it be available on CK3E?!!
-
Hi! How come the CK3E does not show up any CPU-temperature?!! Ok, this feature was not available in 2017: http://forums.deltatau.com/showthread.php?tid=2370 Bot today?!It is quite an important information! Isn't there a way to get to know the temperature of the ARM-cores?! Is ODT thinking of introducing CPU-temperature to CKE3?! Thanks, Anton
-
Meanwhile I could manage to get it to run. I did not properly set up CompTable (using "Compensation Table" in IDE-DeltaTau). For now everything seems to work fine. Thanks nethertheless
-
Hi! I am trying to set up torque-compensation. The Setup-tool shows "LC Setup" but in there I cannot setup/start anything!!? I am using IDE V3.0.1.0 and V4.1.0.24 See pic Any idea? Thanks, Anton
-
I made the same experience on gathering Motor[1].CapturePos with following setup: CK3E PPMAC V2.4.1.2 PPMAC IDE V4.1.0.24 IDE-Plot sets up when pressing "Gather Data"-button: Gather.Type[1]=1542 Gather.Addr[1]=3355995152 ($c8086c10) but would not gather any changes on Motor[1].CapturePos If I manually change Gather.Type[1]=50694 and gather with Gather.Enable=2 any changes on Motor[1].CapturePos are registered correctly. By the way: Motor[1].CapturePos.a=$c8086c13 (3355995155) - how come it does not match Gather.Addr[1]?!
-
Hi! Besides PPMAC IDE and besides PDK (none license-free PowerPmacBuildAndDownload.dll) is there a (documented) license-free way to download an encrypted project to PPMAC?!! Best Regards, Anton
-
Hi Steve! I cant access this link - server not found - any other link to get this document?
-
Hi! After a small dozen $$$*** my CK3E (PPMAC UMAC ARM) connected to an ACC24E3 (both inside UMAC-Rack 5XX-602932-DTE) freezes its foreground-clocks (phase, servo, rti), but background-clock keeps on running. D15 on CPU dark, D13 on ACC24E3 base-board dark One more $$$*** puts it back to full work, some more $$$*** freezes again all foreground-clocks. Anybody has any idea/experience with that?! Using here: Linux version 3.14.28-ipipe (henry@henry-ThinkCentre-M93p) (gcc version 4.6.3 (Ubuntu/Linaro 4.6.3-1ubuntu5) ) #37 SMP Mon Apr 18 14:06:56 PDT 2016 V2.3.2.5 w uboot 0917 Regards, Anton