The text of the manual is confusing in terms of limit specifications: "The 4.7K resistor packs used will allow 12-24V flag inputs. If 0-5V flags are used, then a 1KΩ resistor pack (RP) can be placed in either RP45 or RP46 ..... If these resistor packs are not added, all flags (±Limits, Home, User, and amplifier fault) will be referenced from 0-5V." So do I use a 1K resistor pack or no resistor pack for 0/+5V limits?
  • Replies 2
  • Created
  • Last Reply

Top Posters In This Topic

Top Posters In This Topic

Posted
Answered my own question (partially) by experiment: Without the resistor packs, 5V does not seem to be sensed, but 24V is. Not sure how low I can go. Sounds like another experiment.
  • 4 years later...
Posted
The confusing wording will be changed on the next update. The last sentence should read: "If these resistor packs are not added, all flags (Limits, Home, User, and amplifier fault) will be referenced from 12-24V."