bradp Posted August 6, 2010 Share Posted August 6, 2010 If you want to clear the Motor[5].HomeComplete bit then just send the command sequence #5HmJ/ or #5HmK depending if the motor's final state should be open or closed loop. Link to comment Share on other sites More sharing options...
AnthonyLH Posted June 5, 2019 Share Posted June 5, 2019 On brushless motors I get the message "MOTOR NOT PHASED"... that true ... PhaseFound==0 ... but how do I clear the HomeComplete bit ? i have to set PhaseFound to 1 ? Or do you have another solution ? Thank you Link to comment Share on other sites More sharing options...
curtwilson Posted June 5, 2019 Share Posted June 5, 2019 For a brushless motor commutated by PMAC, at power-on/reset, Motor[x].PhaseFound and Motor[x].HomeComplete are automatically set to 0. To set the PhaseFound bit to 1, you must execute a successful phase referencing operation, either a phasing search move, or a read of an absolute sensor. The PhaseFound bit must equal 1 in order to be able to close the loop for such a motor. And if you can't close the loop, you can't start a homing search move. That is why you see the error reported. So the typical startup procedure for such a motor is to first perform a phasing reference, then a homing search move. The original post had to do with the very unusual case where a homing search move had already been performed successfully, resulting in the HomeComplete bit being set to 1. (For a brushless motor commutated by PMAC, PhaseFound must be 1 in this case.) Then for some reason, the user wants to clear this bit. Link to comment Share on other sites More sharing options...