Hello,

 

i only seem to be able to change the value of the

Acc24E3[0].ServoClockDiv via Tool->System Setup. Changes via the terminal doesn't seem to apply. The Startvalue defined in the setup.pmh is overwritten immediatly.

 

i have to change the value permanently with a terminal command or setup.pmh library.

 

 

Link to comment
Share on other sites

  • Replies 1
  • Created
  • Last Reply

Top Posters In This Topic

Popular Days

Top Posters In This Topic

FEIR,

 

Certain saved parameters in DSPGate3 ASIC which exists in ACC-24E3 are write protected. In order for you to write to these parameters, first you need to provide the write-key to the system. Here is the procedure.

 

1. Set Sys.WpKey=$AAAAAAAA

2. Change the value for the parameters under Gate3. or Acc24E3. as desired.

3. Set Sys.WpKey=0

 

This will change the value on the DSPGate3 ASIC but it will not be retained during a reset or cycle power, unless a SAVE command is issued afterward.

Link to comment