JeffLowe Posted July 21, 2015 Share Posted July 21, 2015 How do I get the IDE to retain the position display window formatting between sessions. Every time I close the IDE and Open it again the # of motors reverts to 4, and the # of decimal places gets set to a default of 2. This is quite painful with 14 defined motors, each requiring 6 or more decimal places. Link to comment Share on other sites More sharing options...
steve.milici Posted July 22, 2015 Share Posted July 22, 2015 Check the file "PositionControl.ini" at the following path: C:\Users\{logon-name}\AppData\Roaming\DeltaTau\INI It should have the date and time when you last closed the IDE. Note that if you open the IDE as another user it will use different credentials and therefore different .INI files. Link to comment Share on other sites More sharing options...
Omron Forums Support Posted July 27, 2015 Share Posted July 27, 2015 Also, make sure the path Steve mentioned isn't write-protected. Link to comment Share on other sites More sharing options...