Adaptive Control - is this working at all?


sutty

Recommended Posts

Hi!

It's one axis. Did tuning unloaded. IDE-Tune-tool says: NominalGain=4800 (unloaded) resp. 550 (loaded with 21,94 kg)

Servo: 16kHz

RTI: 2 kHz

Topology: Motor #4 and Motor #24 (put-through only) cascaded

Set Adaptive-Control-Parameters:

Motor[4].Servo.NominalGain=4800
Motor[4].Servo.EstMinDac=100
Motor[4].Servo.EstTime=160
Motor[4].Servo.MinGainFactor=1
Motor[4].Servo.MaxGainFactor=9
Motor[4].Servo.MinW=0
Motor[4].Servo.MaxW=0
Motor[4].Servo.MinDR=0
Motor[4].Servo.MaxDR=0

Put load with 21,94 kg (total of 100 kg possible) on.

Motor[4].Servo.GainFactor remains all time at 1!!

Motor[4].Servo.EstGain wont go above 0.02

Lowering MinGainFactor would lower GainFactor during accel/deceleration equally to MinGainFactor

By the way setting MinGainFactor = MaxGainFactor = 9 would give a nice and stable setup with 21,94 kg load.

I am really rookie-like - but can anybody show me a good practice example?!!

Would I absolutely have to also set MaxW, MinW, MaxDR and MinDR?

Thanks and regards,

Anton

 

 

Edited by sutty
added motor-topology
Link to comment
Share on other sites

  • Replies 8
  • Created
  • Last Reply

Top Posters In This Topic

MaxW, MinW, MaxDR and MinDR are only used if you intend to implement “Gain Scheduled Adaptive Control”.

I might suspect that at your servo frequency of 16KHz your setting of Motor[4].Servo.EstTime=160 may be too low to acquire sufficient “good data”. The “Power PMAC User’s Manual” suggests 100-500 at the default servo rate of 2.26KHz. Your servo rate is seven times faster. See if increasing this provides better results.

 

Link to comment
Share on other sites

Hi Steve!

I rised EstTime up to 3000 - no improvments at all.

I have to mention again that that ABS(Motor[4].Servo.EstGain) wont rise above 2e-2 in no case.

Motor[4].Servo.NominalGain=4800
Motor[4].Servo.EstMinDac=100
Motor[4].Servo.EstTime=300
Motor[4].Servo.MinGainFactor=1
Motor[4].Servo.MaxGainFactor=5

image.thumb.png.45c8e584aca336bff0f94ff4a32e5a5e.png

 

Motor[4].Servo.NominalGain=4800
Motor[4].Servo.EstMinDac=100
Motor[4].Servo.EstTime=3000
Motor[4].Servo.MinGainFactor=1
Motor[4].Servo.MaxGainFactor=5

image.thumb.png.ec0b5bf2bf0da4a48c45bc6bea370e1d.png

Link to comment
Share on other sites

Yes, it is!

When I set Motor[4].Servo.MinGainFactor = Motor[4].Servo.MaxGainFactor (which forces Motor[4].Servo.GainFactor to that value) = "GainFactor" I calculated according several NominalGain-estimations, and it works from 0 to 100 kg.

For example I tune the 100kg system. Estimate Nominal Gain for 100 kg (around 50) and for 22kg (around 500). So I set Motor[4].Servo.MinGainFactor = Motor[4].Servo.MaxGainFactor = 50/500 = 0.1 which forces Motor[4].Servo.GainFactor = 0.1.

Might the cascading of motor #4 and #24 be a issue?

Edited by sutty
Link to comment
Share on other sites

Hi Steve!

Unfortunately it is quite a deal to de-cascade the 2 loops. At least at the moment I cant spend time to do so. ... I will see in about 1 or 2 weeks and get back to you as soon I know more..

However, Is there a strict no-go for cascaded loops?

Bye, Anton

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...