posalux Posted August 18, 2016 Posted August 18, 2016 Hi, To use the whole table I need to put I226 on -9000000 but then it do not find the zero position of the sensor with the home command. If I put I226 on -8000000 there is no problem. Is there a limit for Ix26? peter
Richard Naddaf Posted August 18, 2016 Posted August 18, 2016 Yes, it is -8388608 to 8388608 just like the manual says. Do you have a copy of the Turbo SRM manual? You can get around this by: - Homing to a smaller or no offset - Jogging to the desired home position - Setting Ixx95 = 0, and issuing an HMZ
Omron Forums Support Posted August 18, 2016 Posted August 18, 2016 Check for "in position" status and perhaps check that following error is minimal before issuing HMZ. I believe it is Ix10 that should be 0 to disable absolute position sensor setup. Note that Ix95 in Non-Turbo is different than Ixx95 in Turbo.
posalux Posted August 18, 2016 Author Posted August 18, 2016 Yes, it is -8388608 to 8388608 just like the manual says. Do you have a copy of the Turbo SRM manual? Sorry ,yes it is in the manual . And I will start the program with a jogging to the end of the table and do a HOMEZ. Thanks for the quickly respons !
posalux Posted August 18, 2016 Author Posted August 18, 2016 Check for "in position" status and perhaps check that following error is minimal before issuing HMZ. I believe it is Ix10 that should be 0 to disable absolute position sensor setup. Note that Ix95 in Non-Turbo is different than Ixx95 in Turbo. I use the table for woodworking and as long the starting point is +/- 1mm it is OK. Thanks for the respons.